    i want to know that it is essential to run earth r bonding wire in emt conduit despite it is good bonding path without having a earth r bonding wire.

    <font color="#a62a2a" size="1">[ July 08, 2004 07:24 AM: Message edited by: electric-ed ]</font>

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    There are three installation conditions under which a separate bonding conductor is required in EMT. They are listed in 10-804(d).

    Ed